    Clothes Dryer. 240 volt, 4800 watts. What size Breakers do I need? Gauge wire?
     
  2. jsstevens

    jsstevens Final Approach PoA Supporter

    Joined:
    May 18, 2007
    Messages:
    6,549

    Display name:
    jsstevens
    That dryer draws 20 amps. You can't load a breaker/circuit above 80% of capacity.

    10 gauge wire and 30 amp breaker is normal for an electric dryer.
     
    Tools, Palmpilot and Shepherd like this.
  3. Sac Arrow

    Sac Arrow Touchdown! Greaser!

    Joined:
    May 11, 2010
    Messages:
    19,491
    Location:
    Charlotte, NC

    Display name:
    Snorting his way across the USA
    Sounds right to me.
     
  4. kmacht

    kmacht Pre-takeoff checklist

    Joined:
    Aug 3, 2009
    Messages:
    370

    Display name:
    Kmacht
    Amps = watts / voltage
    20amps=4800watts/240volts

    As said above, 30 amp breaker and 10 gage wire is standard for a dryer. 20 amps would be the minimum but inrush current is going to be a little more and might trip a fast acting 20amp breaker.
     
  5. Half Fast

    Half Fast Touchdown! Greaser!

    Joined:
    May 7, 2016
    Messages:
    11,000
    Location:
    Central Florida

    Display name:
    Half Fast
    Concur with 30A breaker and 10AWG wire, but be advised that you likely need a GFCI breaker. The 2020 NEC requires GFCI protection for 220V dryer circuits in laundry rooms. Other 120V laundry room circuits require dual AFCI/GFCI protection.
     
    Shepherd likes this.
  6. flyingron

    flyingron Administrator Management Council Member PoA Supporter

    Joined:
    Jul 31, 2007
    Messages:
    23,047
    Location:
    Catawba, NC

    Display name:
    FlyingRon
    Not true. You can't load a breaker over 80% for continuous loads. A dryer is not.

    @Half Fast has it right. And Washington State has been on the 2020 NEC since November of 2020.
     
    Last edited: Mar 2, 2023
  7. luvflyin

    luvflyin Touchdown! Greaser!

    Joined:
    May 8, 2015
    Messages:
    14,513
    Location:
    Vancouver, WA

    Display name:
    Luvflyin
    I had remembered that formula. It was the double breaker thing that was confusing me. I was thinking that two 30’s add up to 60. I know how 240 volt circuits work. Two 120’s out of phase with each other. But now I get it. What I have is the dryer is going to a double 40 now. Old house, many remodels over the years. I’m thinking that circuit used to go to a Stove or something else. Looks like about 8 gauge aluminum wire. It’s pigtailed with wire nuts inside the panel to copper leads to the breaker. I’m thinking I better replace the wire and breaker
     
  8. luvflyin

    luvflyin Touchdown! Greaser!

    Joined:
    May 8, 2015
    Messages:
    14,513
    Location:
    Vancouver, WA

    Display name:
    Luvflyin
    House is in Portland, OR. Built 1910. Last remodel was around 1975. I’m going to sell it.
     
  9. luvflyin

    luvflyin Touchdown! Greaser!

    Joined:
    May 8, 2015
    Messages:
    14,513
    Location:
    Vancouver, WA

    Display name:
    Luvflyin
    Does that have to be done to existing houses? Nothing new is happening here, no remodel. But it’s going up for sale.
     
  10. masloki

    masloki Pattern Altitude

    Joined:
    Aug 23, 2011
    Messages:
    1,656

    Display name:
    DD
    Typically, not until a renovation or other material change would force the work to be made to the new code. But once in a while, a municipality could force owners to upgrade X. I got one of those gifts when my village forced homeowners to ensure no storm drainage went to the sewer systems even though it was common practice in the past.
     
  11. luvflyin

    luvflyin Touchdown! Greaser!

    Joined:
    May 8, 2015
    Messages:
    14,513
    Location:
    Vancouver, WA

    Display name:
    Luvflyin
    That gutter drainage sewer thing happened in Portland many moons ago. Like the 90’s I think
     
  12. jsstevens

    jsstevens Final Approach PoA Supporter

    Joined:
    May 18, 2007
    Messages:
    6,549

    Display name:
    jsstevens
    The cost to add in the GFCI is probably negliegable and avoids any possibility of a home inspector flagging during the sale process. Same wiring, just a different breaker (and slightly different connections in the panel).
     
    Half Fast and Racerx like this.
  13. luvflyin

    luvflyin Touchdown! Greaser!

    Joined:
    May 8, 2015
    Messages:
    14,513
    Location:
    Vancouver, WA

    Display name:
    Luvflyin
    Good point. Gonna replace it anyway, so I'll throw a few more buck$ at it.
     
    Half Fast likes this.
  14. Racerx

    Racerx En-Route

    Joined:
    May 15, 2020
    Messages:
    2,610

    Display name:
    Ernie
    Gotta up the wire gauge if sticking with aluminum, but replacing it like you're doing is better. Sometimes the aluminum corrodes and the connection fails. I hate GFCI breakers, they seem to fail randomly just because. But if you're selling the house I would definitely put one in just because of a home inspection.

    When I built my house in 2016 the energy code/county wouldn't allow the panel to be inside a coat closet. So its on the outside of the closet wall. Took the panel cover off and hung a picture over it. That's apparently better?
     
  15. flyingron

    flyingron Administrator Management Council Member PoA Supporter

    Joined:
    Jul 31, 2007
    Messages:
    23,047
    Location:
    Catawba, NC

    Display name:
    FlyingRon
    You can't put panels in clothes closets or in areas of combustable materials.
     
  16. Bob Noel

    Bob Noel Touchdown! Greaser! PoA Supporter

    Joined:
    Jun 7, 2008
    Messages:
    20,891

    Display name:
    Bob Noel
    Have you priced the difference between a GFCI breaker and a standard breaker?

    I don't think the price difference qualifies as negliegable.
     
  17. jsstevens

    jsstevens Final Approach PoA Supporter

    Joined:
    May 18, 2007
    Messages:
    6,549

    Display name:
    jsstevens
    So I hadn't in a while. GFCI 30A 2P ~$119. 30A 2P ~$15. So a difference of $105. But 15 feet of 10/3 romex is $65. So in the context of the whole job (not knowing how far he's got to run the wire), and compared to having to redo it AFTER the home inspection in today's home market? I stand by negligible. (I admit it was bigger than I expected. Heck, a single pole 20A GFCI is over $50! No wonder everybody uses the outlets to protect circuits. They're around $20.)
     
  18. Half Fast

    Half Fast Touchdown! Greaser!

    Joined:
    May 7, 2016
    Messages:
    11,000
    Location:
    Central Florida

    Display name:
    Half Fast

    Yep. They’re also easier to change when they fail.
     
  19. flyingron

    flyingron Administrator Management Council Member PoA Supporter

    Joined:
    Jul 31, 2007
    Messages:
    23,047
    Location:
    Catawba, NC

    Display name:
    FlyingRon
    By aircraft standards :)
     
  20. asicer

    asicer Final Approach

    Joined:
    Jan 1, 2015
    Messages:
    8,652

    Display name:
    asicer
    And by "change", you mean "swap with the working one that's installed a few feet down but happens to be unused, thus saving yourself $20 and a trip to the big box store", right? :)
     
  21. Pinecone

    Pinecone Pattern Altitude

    Joined:
    May 24, 2022
    Messages:
    1,944
    Location:
    MD

    Display name:
    Pinecone
    Except that 30 amp, 220 volt, GFCI breakers can run well over $100 for just the breaker.

    Even standard 110 volt 15 amp GFCI breakers are a lot more than a 15 amp GFCI outlet.