Been having an ongoing issue for years at this point with my power at work. 240 delta 3ph. The condescending electrical engineer from the local power company blamed it on my equipment being to sensitive to higher voltage and promptly left.
Was about to cut something on the CNC plasma but the power source is giving an error. An error that means either the board is trashed or that I've got an input voltage issue. I check my crane that's on a step up transformer and sure enough, it makes a rattle going up and won't move north/south
The field supervisor or whatever his title is says whenever I'm switched over (whatever that means) that's when I have trouble. When it's normal everything works.
I have both a cheap multimeter and a better true RMS meter. The RMS meter says everything is good. And that's what the power company is saying that everything is good.
Line to line with the RMS meter I'll get 253-250-248.
Line to line with cheap meter I'll get 232-258-256.
When I'm switched back to normal the cheap meter and the RMS meter will match and everything runs happily. The EE's claim that my machines don't like high power is mularkey as previously I measured power 253-254-252 with both meters and everything ran fine. It's only when the meters don't agree and the cheap meter shows imbalance that I have issues.
Any thoughts to take to the power company or utility board?
Was about to cut something on the CNC plasma but the power source is giving an error. An error that means either the board is trashed or that I've got an input voltage issue. I check my crane that's on a step up transformer and sure enough, it makes a rattle going up and won't move north/south
The field supervisor or whatever his title is says whenever I'm switched over (whatever that means) that's when I have trouble. When it's normal everything works.
I have both a cheap multimeter and a better true RMS meter. The RMS meter says everything is good. And that's what the power company is saying that everything is good.
Line to line with the RMS meter I'll get 253-250-248.
Line to line with cheap meter I'll get 232-258-256.
When I'm switched back to normal the cheap meter and the RMS meter will match and everything runs happily. The EE's claim that my machines don't like high power is mularkey as previously I measured power 253-254-252 with both meters and everything ran fine. It's only when the meters don't agree and the cheap meter shows imbalance that I have issues.
Any thoughts to take to the power company or utility board?