The draft inducer on my furnace (Goodman some-model-or-other) was starting to make some noise a few weeks ago, so I replaced it.
I also knew that the flame sensor was on its last leg (I'd already cleaned it, but it was still hit-or-miss whether the furnace would sense the flame before the third failed attempt shut it down for an hour), so I replaced that, too.
In addition, I knew that the burners hadn't been cleaned since... well, ever, as far as I know, so I cleaned them. I used some spray stuff and stiff bristle brushes, plus some compressed air to blow the little bits of stuff out of them. They were rusty on the end with the little holes. Now they are not.
In the process of cleaning the burners I broke the ignitor, so I replaced that, too. I think it was the one Noah used on the ark, so probably it needed to be replaced anyway.
I also peered inside the firebox, which looked remarkably clean, so I did nothing to it.
The propane guy also replaced the low-pressure regulator and put some isopropanol in the tanks because he suspected there was some water in there and that the regulator was freezing. He made a second trip after inspecting the system and didn't charge me for that work, so I'm assuming it was necessary.
The furnace is working fine now, the flames are nice and blue, and it's nice and quiet. I change the air filter once a month. Is there anything else I might want to do or have done to be winter ready?
The above (other than the ignitor, which I broke) were all the propane guy suggested I do after looking over the furnace. But second opinions are always nice.
Thanks.
Rich
I also knew that the flame sensor was on its last leg (I'd already cleaned it, but it was still hit-or-miss whether the furnace would sense the flame before the third failed attempt shut it down for an hour), so I replaced that, too.
In addition, I knew that the burners hadn't been cleaned since... well, ever, as far as I know, so I cleaned them. I used some spray stuff and stiff bristle brushes, plus some compressed air to blow the little bits of stuff out of them. They were rusty on the end with the little holes. Now they are not.
In the process of cleaning the burners I broke the ignitor, so I replaced that, too. I think it was the one Noah used on the ark, so probably it needed to be replaced anyway.
I also peered inside the firebox, which looked remarkably clean, so I did nothing to it.
The propane guy also replaced the low-pressure regulator and put some isopropanol in the tanks because he suspected there was some water in there and that the regulator was freezing. He made a second trip after inspecting the system and didn't charge me for that work, so I'm assuming it was necessary.
The furnace is working fine now, the flames are nice and blue, and it's nice and quiet. I change the air filter once a month. Is there anything else I might want to do or have done to be winter ready?
The above (other than the ignitor, which I broke) were all the propane guy suggested I do after looking over the furnace. But second opinions are always nice.
Thanks.
Rich