The reason the spec sheet can't tell ya is because it can be ordered in multiple configurations. Drives add to the power it needs and it can have different drive cages, can be had with and without hardware RAID, even the average room temperature will change the power draw because the fans are variable speed depending on internal temperature and go faster or slower even depending on CPU load. Etc.
Two possibilities:
- Rate the UPS for the max power draw.
- Measure with a clamp on AC ammeter on all of the power leads, assuming no configuration changes will be occurring and/or padding the result for future disk expansion if it isn't full yet.
The spec sheet does show that three options were available for the power supplies: 500W, 800W, or 1400W max. You may also want to pull one and look at see which type you're using.
An interesting side note: If it's in an air conditioned room or server room, keep in mind that when the site loses power it also typically loses cooling, and anything on UPS is now an excellent room warmer... We've been discussing this problem for one of our small office server closets... Can plan to keep things running for a while, but they're going to need power for the PCs that access those servers also, and not to forget to rate the genset that will probably demand, to run the server room A/C, and wire it into the transfer switch setup... Always something...